Re: 200A " help"
If your 200 amp panel is a standard panelboard/loadcenter (not I-line gear/panelboard, etc), I believe you will find a 3 pole 100 is the largest branch breaker available ); therfore, if you wish to feed it as you describe, you would most likely set a 100 amp MLO panel (loadcenter)..with neutral and ground seperation.
There are other ways to accomplish the same thing (sub-feed lugs, etc),but I believe this might be considered "standard"
as for code reference...NEC lol..I guess 240-20, 21 would be the primary guide. (edited for code reference)
[ September 01, 2005, 06:44 AM: Message edited by: augie47 ]