Q quantum Senior Member Location LA Nov 10, 2017 #1 A 200A Service with a 200A Main Service Breaker feeding a 125A Main Distribution Panel. Is there anything in the wrong with this? Would the conductors be sized for the Main Service Breaker or the Panel?
A 200A Service with a 200A Main Service Breaker feeding a 125A Main Distribution Panel. Is there anything in the wrong with this? Would the conductors be sized for the Main Service Breaker or the Panel?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Nov 10, 2017 #2 The panel is required to be protected at 125 amps or less, does it have a main?
Q quantum Senior Member Location LA Nov 10, 2017 #3 infinity said: The panel is required to be protected at 125 amps or less, does it have a main? Click to expand... Yes.
infinity said: The panel is required to be protected at 125 amps or less, does it have a main? Click to expand... Yes.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Nov 10, 2017 #4 So unless one of the tap rules apply you'll need 200 amp conductors to feed the 125 amp CB.