I have a 200A service just wondering if i can go down to a 2/0 thhn size wire. 2/0 is rated 195A and 3/0 is 225A.
I have a 200A service just wondering if i can go down to a 2/0 thhn size wire. 2/0 is rated 195A and 3/0 is 225A.
I have a 200A service just wondering if i can go down to a 2/0 thhn size wire. 2/0 is rated 195A and 3/0 is 225A.
But you cannot obtain the 176 as the cap for a 75°C termination of 2/0 copper is 175A.Most likely yes. As mentioned if it's a dwelling unit, you get to use smaller wire. Also the next size up rule comes into play which allows 176-199 amp wire on a 200 amp main breaker as long as it exceeds the load calc.
But you cannot obtain the 176 as the cap for a 75°C termination of 2/0 copper is 175A.
I have a 200A service just wondering if i can go down to a 2/0 thhn size wire. 2/0 is rated 195A and 3/0 is 225A.