rszimm

Member
Location
Tucson, AZ
I’ve got a 400A main panel. Technically it’s a 200A/200A split main panel. The secondary 200A goes to a sub panel that essentially serves as the main house panel. The actual primary 200A is more or less unused. There’s a 40A solar circuit on it and a 15A GFCI breaker that goes to a shed.

So I’m building a guest house/shop and in a perfect world I’d like to pull wires for a full 200A subpanel at the guest house from the pretty much unused 200A main. So my question is if I need a 200A breaker installed in the main panel, or can I tap directly off the main 200 A breaker? (Sub feed block). It would seem the 200A main breaker protects the wires so a second 200A breaker seems redundant. However, the 40A solar has me concerned. Would I have to size up the wire to handle 240A? Also, I think the largest sub feed block you can get for my Eaton panel is a 225A block, which is less than the full 240A.
 
I’ve got a 400A main panel. Technically it’s a 200A/200A split main panel. The secondary 200A goes to a sub panel that essentially serves as the main house panel. The actual primary 200A is more or less unused. There’s a 40A solar circuit on it and a 15A GFCI breaker that goes to a shed.

So I’m building a guest house/shop and in a perfect world I’d like to pull wires for a full 200A subpanel at the guest house from the pretty much unused 200A main. So my question is if I need a 200A breaker installed in the main panel, or can I tap directly off the main 200 A breaker? (Sub feed block). It would seem the 200A main breaker protects the wires so a second 200A breaker seems redundant. However, the 40A solar has me concerned. Would I have to size up the wire to handle 240A? Also, I think the largest sub feed block you can get for my Eaton panel is a 225A block, which is less than the full 240A.

If you install a 200 amp breaker to protect your feeder to the guest house the 125 % of the solar output current would not be an issue on your guest house feeder

in other words the feeder would not be a tap if protected on the supply end (main service panel)
 
If you install a 200 amp breaker to protect your feeder to the guest house the 125 % of the solar output current would not be an issue on your guest house feeder

in other words the feeder would not be a tap if protected on the supply end (main service panel)

Makes sense except I believe BR breakers only go to 150A.
 