For a 200 amp underground service 3/0 thhn is rated for 225A and 2/0 is rated for 195. Could i use the 2/0 or do i have to use the 3/0.
If they are feeders, then I would suggest you check one of the following tables based on the kind of wire/cable you are putting in the duct. Underground has heat dissipation issues. Detail 1 is a single duct without others nearby.
TABLE B.310.15(B)(2)(6) Ampacities of Three Insulated Conductors, Rated 0 through 2000 Volts, Within an Overall Covering (Three-Conductor Cable) in Underground Electrical Ducts (One Cable per
Electrical Duct) Based on Ambient Earth Temperature of 20C (68F), Electrical Duct Arrangement in
Accordance with Figure B.310.15(B)(2)(2), Conductor Temperature 75C (167F)
and
TABLE B.310.15(B)(2)(7) Ampacities of Three Single Insulated Conductors, Rated 0 Through 2000
Volts, in Underground Electrical Ducts (Three Conductors per Electrical Duct) Based on Ambient Earth
Temperature of 20C (68F), Electrical Duct Arrangement in Accordance with Figure B.310.15(B)(2)(2),
Conductor Temperature 75C (167F)
Maybe I don't understand the issue, but an underground duct is conduit and is often PVC.OP didn't mention "ducts" he only mentioned underground which usually is just conduit, mainly PVC.
For a 200 amp underground service 3/0 thhn is rated for 225A and 2/0 is rated for 195. Could i use the 2/0 or do i have to use the 3/0.
If it is residential their is a chart in the nec that you need to apply.
Sent from my SM-T350 using Tapatalk
Chart disappeared in 2014 NEC. 83% of normal conductor ampacity is the rule now, but still gives you same size as the charts did before any ampacity adjustments come into play.Don't always go to 310-16, if it is residential you have an alternative.
Sent from my SM-T350 using Tapatalk
Using a pre 2002 code book aren't you.Don't always go to 310-16, if it is residential you have an alternative.