Per table 310.12 seems like 4/0 aluminum should be the correct size needed for a 200a underground feeders from a meter main to the sub panel in the house? Roughly 150ft away.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I believe you mean 310.15(B)(16). A residence is allowed a factor of 83% so for a 200 amp service you only need a conductor rated 166 amps. At 75C 4/0 AL is rated 180 amps so it is fine. There is a bit of Voltage drop you may want to consider if the calculated load is very high.
 

Cnorris0916

Member
Location
Oregon
Occupation
Electrician
Yes sorry, as for voltage drop per the calculation at 200amp(s) it's still over the 166a so I figured it won't be a problem. Just double checking. Thanks for the input!
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Also even without the 83% rule you can go to the next standard size OCPD which is 200 amps on a #4/0, 180 amp conductor.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I believe you mean 310.15(B)(16). A residence is allowed a factor of 83% so for a 200 amp service you only need a conductor rated 166 amps. At 75C 4/0 AL is rated 180 amps so it is fine. There is a bit of Voltage drop you may want to consider if the calculated load is very high.
Dwelling unit service conductors, and the 83% rule, were in 310.15(B)(7) in the 2017 code but those rules moved to 310.12 in the 2020 and Table 310.12 is correct. They brought the table back, so you only need to use the 83% rule were the you have to adjust or correct the service conductor ampacity for more than 3 conductors in a raceway or cable, or for elevated temperature.
 