So I'm working on finding out what the available fault current is BUT, I've got a very simple 12kV oneline comprised of a single incomming line and two outgoing feeders each to a 2500kVA transformer. Switchgear is to be S&C type fusible switch. So, it's a given that I'll have 150E fuses for the two feeders. The question becomes what is the minimum size upstream breaker I can use and be selective. Would like to keep this as small as possible owing to some bottle necks I'm running into with the utility. Would like to make it therefore 200E. Given a peak load of 4.2MVA and given that that equates to 198A at 12.2kV voltage we're at, a 200E fuse ought to work fine. My concern is the inrush of potentailly two 2500kVA transformers starting up at the same time. If I take that at 2 times 12 times FLA, I get 3000A for an inrush point. That right about on the 200E line. Am I getting carried away worrying about this fuse tripping in the event of a utility outage and then restart? Besides, isn't it only 12 times the FLA on the first start up ever and after that considerably less.