elja
New member
- Location
- United States
I am involved in a construction dispute. Fire alarm plans were approved subject to 2010 NFPA 72. Plans show addressable SLC with addressable notification devices tapped onto the SLC circuit. The developer wants separeated NAC circuit, from the SLC circuit. Contractor says, show us where in the 2010 NFPA 72 that it is disallowed to run as many notification devices as we need from the SLC. The notification devices have their own power supply, address with the FACP, backup power, and isolation modules. I am of the understanding that the contractor is correct, and it is the reviewer / plan checker that needs to demonstrate if an item is in non-compliance, rather than the converse where the obligation is on the designer to prove their design is compliant with the intent and the design is at least equivalent in performance to the prescriptive intent. I am still of the opinion that the 2010 NFPA 72 allows addressable notification devices to be attached to SLC's. Consider that Grinnell makes such an addressable notification circuit module OXA-504SDA. thank you for any help you share, here. Elja