In a recent Mike Holt 2011 NEC Q&A, an example was provided for a 40 amp bkr with the ungrounded conductors increased from #8 to #6, the equip ground conductor (EGC) had to increase proportionately from #10 to #8. This is to the letter of the Code. Is there a reason why a 60 amp bkr using #6 conductors can use a #10 EGC (per table 250.122), while a 40 amp bkr with #6 conductors must use a #10 EGC?