construct
Senior Member
- Location
- Branson, Missouri
Says that NM, NMC, and NMS cables are not allowed in dropped or suspended ceilings in other than one and two and multifamily dwellings. I'm trying to find some clarity between "dropped" and "suspended". I think that a suspended ceiling is a drop ceiling, but a drop ceiling is not necessarily a suspended ceiling. Some manufacturers refer to their suspended ceilings as drop ceilings.
My scenario is that I'm looking at a 4 story hotel. The bottom of the floor joists above are sheetrocked, but in the bathrooms, the ceiling is then dropped another 1.5 ft, framed and sheetrocked and romex used in the wiring method. I think this complies with 334.10(3) in that it is concealed behind a thermal barrier of material with a 15 minute finish rating.
Thoughts and input would be appreciated. :?
My scenario is that I'm looking at a 4 story hotel. The bottom of the floor joists above are sheetrocked, but in the bathrooms, the ceiling is then dropped another 1.5 ft, framed and sheetrocked and romex used in the wiring method. I think this complies with 334.10(3) in that it is concealed behind a thermal barrier of material with a 15 minute finish rating.
Thoughts and input would be appreciated. :?