inspector23
- Temecula, CA
2011NEC 705.12(D)(7) "..In systems with panelboards connected in series, the rating of the first overcurrent device directly connected to the output of a utility-interactive inverter(s)shall be used in the calculations for all busbars and conductors. ..."
I have an inverter output connection with a 30A OCPD interconnecting to a 100A MLO subpanel in a garage.The feeder for the subpanel comes from the MSP, protected by a 100A OCPD located on the MSP busbar next to the middle-fed main breaker (200A MB, 200A rated bus service panel).My interpretation of this code section, this configuration will not be allowed since I have to use the 30A OCPD for calculations for ALL busbars and conductors, not just the subpanel, but the MSP as well. Since the MSP has a 200A rated bus and a 200A MB and it is a middle fed configuration, it is not eligible for the 120% rule. I understand there may be a possibility of downsizing the MB after existing load calculations justify, but as presented, it is not compliant.
AT least that is my interpretation of this code section. I am questioning if my interpretation of "ALL busbars and conductors" is valid. Any comments/insights/ viewpoints welcome.
Thanks -
Thanks -