I found this while surfing today. I thought it might interest some.
How could these rules ever be imposed on premises wiring systems when we have zero control over the voltage drop that exists on the outdoor distribution system?
My vote is for rejection.
I thought impedence was only used for AC. Seems like the definition could be reworded to include DC voltage drop too.100 Definitions I. General Voltage Drop. Voltage-drop is the difference in the voltage of a circuit created by the connection of a resistor or load to the circuit. Voltage-drop may be measured by connecting a known resistance at a certain point in a circuit. Since the applied resistance is a constant, the change in circuit voltage that is created by the known resistance can be calculated as the impedance of the circuit itself from the source of the voltage to the point of the measurement.
How could these rules ever be imposed on premises wiring systems when we have zero control over the voltage drop that exists on the outdoor distribution system?
My vote is for rejection.
How could these rules ever be imposed on premises wiring systems when we have zero control over the voltage drop that exists on the outdoor distribution system?
(A) Branch Circuits Not More Than 600 Volts.
(5) Maximum Permissible Voltage-Drop. Conductors shall be sized such that voltage-drop at the furthest outlet on a 120-volt branch circuit shall not exceed 8.0% to ensure sufficient available short-circuit or fault current to facilitate the operation of the branch circuit overcurrent protection device as required by Article 250.4(A)(5).
Who cares about VD on the POCO side? That's their problem.
Who cares about VD on the POCO side? That's their problem.
You must live in a neighborhood that has updated power lines, VD is an issue in many older tracks where when Joe 4 doors down runs a power tool, your lights dim. And the POCO could careless.
The section applies to the branch circuit, not the total.
If the voltage at the breaker terminal is 115 you could drop 8% more.
I care because they supply a certain amount of voltage drop to us already. Circuit length is from the source transfomer terminals to the last receptacle on the circuit.
Case in point. This last summer we were getting a final inspection on a duplex that we just finished. The inspector had one of those SureTest gizmos and he plugged it into the bedroom receptacle and did the test. Fail. We raised hell about it because as it turns out we were the very last house on the poco run. The transformer was also a good 200 feet down the road. To make matters worse it happened to be one of the hottest days of summer and AC's were running. Of course there is going to be voltage drop. :roll:
But the branch circuit is still part of an overall system, and part of that system is beyond our control. If we can't control one part of the system the we can't control any part of it.
The NEC could care less about the POCO side of the service.
Pete Article 210 applies only to BRANCH CIRCUITS, the proposed section says BRANCH CIRCUIT and the NEC has a definition of BRANCH CIRCUIT.
But it is not the ECs problem and that prosed section excludes the service and feeder voltages. :smile:
I'm well aware of that too. You're just not seeing it from my perspective.
I'm well aware of that too. You're just not seeing it from my perspective, which happens to be the correct perspective.![]()
I can see the point of VD rules in the NEC for quick operation of OCPD's. But I think this one will be hard to enforce.