"Delta-Connected Service. The grounded conductor of a 3-phase, 3-wire delta service shall have an ampacity not less than that of the ungrounded conductors."
What grounded conductor are they referring to in a 3-phase, 3 wire delta service?
We have a current 3-phase, 3-wire delta service to a building. I understand that a ground fault on any single phase creates a corner grounded system, but doesn't that also create objectionable current? How is this handled if at all since a single phase ground fault would not trip any breakers?
Thanks,
What grounded conductor are they referring to in a 3-phase, 3 wire delta service?
We have a current 3-phase, 3-wire delta service to a building. I understand that a ground fault on any single phase creates a corner grounded system, but doesn't that also create objectionable current? How is this handled if at all since a single phase ground fault would not trip any breakers?