2014 406.4(D)(3)

Status
Not open for further replies.

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
1. Section: 406.4(D)(3)
2. Deleted Text
3. Delete the exception.
4. The exception is unnecessary, as (D)(3) does not require a GFCI receptacle to be installed at the location of the replaced receptacle. (D)(3) requires a GFCI protected receptacle, which per the main rule can simply be a GFCI breaker and a duplex receptacle.
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Sorry: per Alexander's requirement, numbered off per line of proposal.

1. Section Number
2. New/Edited/Deleted text recommended
3. Proposed text or action
4. Substantiation.

Typing on the phone and being lazy again. :)
 