110.16 Arc-Flash Hazard Warning. Electrical equipment, such as switchboards, switchgear, panelboards, industrial control panels, meter socket enclosures, and motor control centers, that are in other than dwelling units, and are likely to require examination, adjustment, servicing, or maintenance while energized shall be field or factory marked to warn qualified persons of potential electric arc flash hazards. The marking shall meet the requirements in 110.21(B) and shall be located so as to be clearly visible to qualified persons before examination, adjustment, servicing, or maintenance of the equipment. [ROP 9?14a, ROP 1?102, ROP 1?105, ROP 1?107]
I am concerned that this section may allow the requirements of the new 110.16 not to apply to massive service entrance installations in multi-family apartments of condos. Is a service entrance and meter bank for twenty 100A 120/240 exempt from this requirement?
I am concerned that this section may allow the requirements of the new 110.16 not to apply to massive service entrance installations in multi-family apartments of condos. Is a service entrance and meter bank for twenty 100A 120/240 exempt from this requirement?