I would like confirmation on my interpretation of NEC 310.15(A)(2) and which ampacity table should be used for the base value. Below is the text in the 2014 NEC that I have found to support my interpretation followed by an example. The example is used to help show why different ampacity tables would be used for determining the allowable ampacity for the whole length of the circuit.
1) 310.15(A)(2) Selection of Ampacity ?Where more than one ampacity applies for a given circuit length, the lowest value shall be used.
2) 310.15(B)(3)(a) ?Where the number of current-carrying conductors in a raceway or cable exceeds three, or where single conductors or multiconductor cables are installed without maintaining spacing for a continuous length longer than 24 in. and are not installed in a raceway, the allowable ampacity of each conductor shall be reduced as shown in Table 310.15(B)(3)(a).?
3) The note in Table 310.15(B)(3)(a), ?Percent of Values in Table 310.15(B)(16) through Table 310.15(B0(19)??
The above language appears to allow the typical adjustment factors to be applied to Table 310.15(B)(17) and Table 310.15(B)(16) for a circuit made of multiple single conductors cables that are installed in an open cable tray and in conduit for different sections of the circuit. For example, a group of twelve #10 AWG copper single PV Wire cables are routed together in a 2? wide, solid bottom cable tray under the ground mounted PV array. Then the same group of cables transition into underground conduit. I?ll work through specific calculation for the two sections to determine the lowest value per 310.15(A)(2).
Cable Tray Section;
The ambient temperature is elevated near the PV module so I used 14?C adder from Table 310.15(B)(3)(c) for guidance. Therefore, the ambient temperature is ASHRAE 2% plus 14?C, 34? + 14?C = 48?C. Using Table 310.15(B)(17) with the adjustment factors we get the following ampacity; 55A x 0.82 x 0.5 = 22.6A
Underground Conduit Section:
The ambient temperature is 34? for the conduit section. Using Table 310.15(B)(16) with the adjustment factors we get the following ampacity; 40 x 0.96 x 0.5 = 19.2A
Therefore the ampacity of the #10 AWG copper single PV Wire cable in this example is 19.2A for the whole length of the circuit, including the cable tray section. Please confirm my method of selecting the appropriate ampacity and adjustment factor tables.
Thank you.
1) 310.15(A)(2) Selection of Ampacity ?Where more than one ampacity applies for a given circuit length, the lowest value shall be used.
2) 310.15(B)(3)(a) ?Where the number of current-carrying conductors in a raceway or cable exceeds three, or where single conductors or multiconductor cables are installed without maintaining spacing for a continuous length longer than 24 in. and are not installed in a raceway, the allowable ampacity of each conductor shall be reduced as shown in Table 310.15(B)(3)(a).?
3) The note in Table 310.15(B)(3)(a), ?Percent of Values in Table 310.15(B)(16) through Table 310.15(B0(19)??
The above language appears to allow the typical adjustment factors to be applied to Table 310.15(B)(17) and Table 310.15(B)(16) for a circuit made of multiple single conductors cables that are installed in an open cable tray and in conduit for different sections of the circuit. For example, a group of twelve #10 AWG copper single PV Wire cables are routed together in a 2? wide, solid bottom cable tray under the ground mounted PV array. Then the same group of cables transition into underground conduit. I?ll work through specific calculation for the two sections to determine the lowest value per 310.15(A)(2).
Cable Tray Section;
The ambient temperature is elevated near the PV module so I used 14?C adder from Table 310.15(B)(3)(c) for guidance. Therefore, the ambient temperature is ASHRAE 2% plus 14?C, 34? + 14?C = 48?C. Using Table 310.15(B)(17) with the adjustment factors we get the following ampacity; 55A x 0.82 x 0.5 = 22.6A
Underground Conduit Section:
The ambient temperature is 34? for the conduit section. Using Table 310.15(B)(16) with the adjustment factors we get the following ampacity; 40 x 0.96 x 0.5 = 19.2A
Therefore the ampacity of the #10 AWG copper single PV Wire cable in this example is 19.2A for the whole length of the circuit, including the cable tray section. Please confirm my method of selecting the appropriate ampacity and adjustment factor tables.
Thank you.