L Lee T. New member Location Rockville, Md. May 31, 2017 #1 How does one protect kitchen counter top receptacles using a gfci per 210.8.A.6 and a cafci per 210.12.A at the same time?
How does one protect kitchen counter top receptacles using a gfci per 210.8.A.6 and a cafci per 210.12.A at the same time?
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor May 31, 2017 #2 They make a breaker that is both Gfci and Afci . You can also use an afci breaker then use a gfci receptacle at the first receptacle
They make a breaker that is both Gfci and Afci . You can also use an afci breaker then use a gfci receptacle at the first receptacle
electricalist Senior Member Location dallas tx May 31, 2017 #3 Around here a dual function cost less than just an AFCI. It's becoming the norm to all dual function. Sent from my iPhone using Tapatalk
Around here a dual function cost less than just an AFCI. It's becoming the norm to all dual function. Sent from my iPhone using Tapatalk
al hildenbrand Senior Member Location Minnesota Occupation Electrical Contractor, Electrical Consultant, Electrical Engineer May 31, 2017 #4 And, if you are only replacing the above counter receptacle device in an existing outlet box, using a dual function Outlet Branch Circuit Arc Fault / Ground Fault receptacle device will suffice, per 2014 NEC 406.4(D)
And, if you are only replacing the above counter receptacle device in an existing outlet box, using a dual function Outlet Branch Circuit Arc Fault / Ground Fault receptacle device will suffice, per 2014 NEC 406.4(D)