2011 cycle 590.6(A)
(3) Receptacles on 15-kW or less Portable Generators. All 125-volt and 125/250-volt, single-phase, 15-, 20-, and 30-ampere receptacle outlets that are a part of a 15-kW or smaller portable generator shall have listed ground-fault circuit-interrupter protection for personnel. All 15- and 20-ampere, 125- and 250 volt receptacles, including those that are part of a portable generator, used in a damp or wet location shall comply with
406.9(A) and
(B). Listed cord sets or devices incorporating listed ground-fault circuit-interrupter protection for personnel identified for portable use shall be permitted for use with 15-kW or less portable generators
manufactured or remanufactured prior to
January 1, 2011.