2014 section 424.22

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have Dayton 2YU79 30kw 208V three phase electric unit heater. The branch circuit breaker is 100A. 424.22(B) says to provide no more than 60A else sub divide. I am not really sure why this would not have been done for this heater?


All reference NEC 2014


Sent from my iPhone using Tapatalk
 
You're sure it's not done within the unit or as a separate part from the manufacturer?

424.22(C)
"(C) Overcurrent Protective Devices. The supplementary overcurrent
protective devices for the subdivided loads specified in
424.22(B) shall be (1) factory-installed within or on the heater
enclosure or supplied for use with the heater as a separate
assembly by the heater manufacturer;... "
 