- Location
- Tennessee NEC:2017
- Occupation
- Semi-Retired Electrician
(4) Garage Branch Circuits. In addition to the number of
branch circuits required by other parts of this section, at least
one 120-volt, 20-ampere branch circuit shall be installed to
supply receptacle outlets in attached garages and in detached
garages with electric power. This circuit shall have no other
outlets.
Exception: This circuit shall be permitted to supply readily accessible
outdoor receptacle outlets.
Does this mean that the lights in a dwelling garage can't be on the same circuit as the receptacles?
We are moving to the 2017 next month (Oct 1) and I'm trying to get up to speed. We are being overwhelmed as we are currently on the 2008 and skipping the 2011, 2014, and going straight to the 17.