We have a project where the main service is 200 amps. 100 amp sub feed to a 125amp sub panel in a barn. My electrician installed a 12KW system on the barn. (50amp solar breaker)
125x1.20=150amps - 100 amp main= 50amps, solar breaker is fine. Question is, do we have to relocate the 100 amp feeder to the bottom of the main panel and derate the 200 amp main to a 175 to be in compliance. I have read 705 (B) in its entirety and it is vague to multiple panels when back feeding from the farthest point. We have passed multiple inspections doing so, and this new inspector is questioning this. I do see his point as to where the power is coming from. The 100amp is backfed but NEC is unclear. In 705.12 (B) (3) it does say it has to be identified as we are supplying power to another busbar. So it seems to me it applies to all panelboards involved. Thoughts?
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Electrical Engineer - Photovoltaic Systems
We have a project where the main service is 200 amps. 100 amp sub feed to a 125amp sub panel in a barn. My electrician installed a 12KW system on the barn. (50amp solar breaker)
125x1.20=150amps - 100 amp main= 50amps, solar breaker is fine. Question is, do we have to relocate the 100 amp feeder to the bottom of the main panel and derate the 200 amp main to a 175 to be in compliance. I have read 705 (B) in its entirety and it is vague to multiple panels when back feeding from the farthest point. We have passed multiple inspections doing so, and this new inspector is questioning this. I do see his point as to where the power is coming from. The 100amp is backfed but NEC is unclear. In 705.12 (B) (3) it does say it has to be identified as we are supplying power to another busbar. So it seems to me it applies to all panelboards involved. Thoughts?
You are correct; you have to qualify every busbar between the PV and the service in compliance with 705.12(D)(2)(3) a, b, c, or d in the 2014 NEC. It's in 705.12(B) in 2017.
 

pv_n00b

Senior Member
Location
CA, USA
The same reasoning that drives the CB position in the sub-panel that is being back-fed directly from the PV system also applies to all panels in the PV current path back to the utility interconnection. It's hit or miss if AHJs apply this correctly so some contractors can get through quite a few projects before running into an AHJ who points out this requirement.
 