Ohms law
Senior Member
- Location
- Sioux Falls,SD
I am wondering if anyone can clarify 210.63*Heating, Air-Conditioning, and Refrigeration Equipment Outlet. A 125-volt, single phase, 15- or 20-ampere-rated receptacle outlet shall be installed at an accessible location for the servicing of heating, air-conditioning, and refrigeration equipment. The receptacle shall be located on the same level and within 7.5 m (25 ft) of the heating, air-conditioning, and refrigeration equipment. The receptacle outlet shall not be connected to the load side of the equipment disconnecting means.
When it states shall not be connected to load side of equipment disconnecting means, can I supply a 120vac receptacle off the line side and meet code? The Make Up unit itself is 120vac and is heat only.
Sent from my SM-G930V using Tapatalk
When it states shall not be connected to load side of equipment disconnecting means, can I supply a 120vac receptacle off the line side and meet code? The Make Up unit itself is 120vac and is heat only.