Hello, I am just looking to make sure I'm understanding things right.
250.52 (A)(3) CEE allows either 1/2 inch minimum conductive steel reinforcement at the bottom of the footing (20 ft min) or 20 ft of #4 bare copper. (If a new foundation is being built we require the use of the CEE.)
250.52 (A)(5) defines acceptable rod and pipe electrodes. (In remodels where a CEE does not exist and no foundation work is being done we accept rods.)
250.53 (A) defines GES requirements. (A)(2) defines supplemental electrode requirements. (E) states that the supplemental electrode bonding connection does not need to be larger than 6 AWG copper.
250.66 (A) states that connections to Rod that does not extend to other types of electrodes shall not be required to be larger than 6 AWG copper. (B) States that that if the CEE does not extend... then it is not required to be larger than 4 AWG copper.
So if I am understanding all of this correct, and all of those conditions are met, then the grounding electrode conductor does not need to be larger than 6 AWG copper for rods and 4 AWG copper for CEE regardless of the requirements in table 250.66.
I'm digging into Table 250.102(C)(1) next and it appears that there are not similar "exceptions" for bonding jumpers, correct?
Am I on track? Thanks very much.
P.S. I'm headed out for the weekend so I won't be able to see replies till Monday morning.
250.52 (A)(3) CEE allows either 1/2 inch minimum conductive steel reinforcement at the bottom of the footing (20 ft min) or 20 ft of #4 bare copper. (If a new foundation is being built we require the use of the CEE.)
250.52 (A)(5) defines acceptable rod and pipe electrodes. (In remodels where a CEE does not exist and no foundation work is being done we accept rods.)
250.53 (A) defines GES requirements. (A)(2) defines supplemental electrode requirements. (E) states that the supplemental electrode bonding connection does not need to be larger than 6 AWG copper.
250.66 (A) states that connections to Rod that does not extend to other types of electrodes shall not be required to be larger than 6 AWG copper. (B) States that that if the CEE does not extend... then it is not required to be larger than 4 AWG copper.
So if I am understanding all of this correct, and all of those conditions are met, then the grounding electrode conductor does not need to be larger than 6 AWG copper for rods and 4 AWG copper for CEE regardless of the requirements in table 250.66.
I'm digging into Table 250.102(C)(1) next and it appears that there are not similar "exceptions" for bonding jumpers, correct?
Am I on track? Thanks very much.
P.S. I'm headed out for the weekend so I won't be able to see replies till Monday morning.