I am having a discussion with an inspection supervisor about the allowable ampacity of #8 TC-ER cable in a raceway for a one-family dwelling.
The inspector's understanding is that i) if it's in a one-family dwelling, ii) if it contains power and control conductors, and iii) if is identified for pulling through structural members then I must follow the stipulation to use the Part II of Article 334 and thus use the 60° Column. I object on two points:
The first is my understanding of the structure of the NEC, which is that permissions, by their nature, never disallow things [90.5(B)]. 336.10(3) allows me to put the cable in a raceway, and 336.80 tells me the ampacity must be in accordance with 310.15 (75° Column). The existence of 336.10(9) is irrelevant if I am not using it.
The second is specific, which is that 336.10(9) is for exposed runs, as clarified in 336.12(2). If I am using it in a raceway, then it is obviously not an exposed run.
Regards,
Barklie Estes
The inspector's understanding is that i) if it's in a one-family dwelling, ii) if it contains power and control conductors, and iii) if is identified for pulling through structural members then I must follow the stipulation to use the Part II of Article 334 and thus use the 60° Column. I object on two points:
The first is my understanding of the structure of the NEC, which is that permissions, by their nature, never disallow things [90.5(B)]. 336.10(3) allows me to put the cable in a raceway, and 336.80 tells me the ampacity must be in accordance with 310.15 (75° Column). The existence of 336.10(9) is irrelevant if I am not using it.
The second is specific, which is that 336.10(9) is for exposed runs, as clarified in 336.12(2). If I am using it in a raceway, then it is obviously not an exposed run.
Regards,