Your opinion please. The way I read this, SEU & SER, above size 10, we may now use the 75 degree rating. So #4 SER Al. can now be used as 65 degrees and connected to a 70 amp breaker. :happyyes:
Your are reading it correctly. SE cable is now at 75C.....
Your are reading it correctly. SE cable is now at 75C.....
I know that Terry Cromer our NC Association of Electrical Contractors director was very vocal on this as he has been for many code cycles.Finally some common sense. This will probably change again in the 2020. :roll:
Amazing how long that took. I will be interesting to go back and read the ROPs to see the reasoning for the 1st change and then the reversal. Its the same cable now as it was in '08 (or '05, I can't recall) when it became restrictive.
This was pushed by the wire and cable folks......Made sense since the conductors inside are more than likely 75C and in some cases even 90C insulation. The argument was that (and their still is not any known) type SE Cable was evaluated using the same specifications as Type NM-B and as such the 60C was to be used...due to their similarity. However, no one could produce anything for SE as tested like NM-B so that lack of information supported the face the inners are again rated for 75C or even 90C from some manufacturers.I know that Terry Cromer our NC Association of Electrical Contractors director was very vocal on this as he has been for many code cycles.
This was pushed by the wire and cable folks......Made sense since the conductors inside are more than likely 75C and in some cases even 90C insulation.
I thought Southwire were the ones that did the study that was the substantiation for the 60C
This was pushed by the wire and cable folks......Made sense since the conductors inside are more than likely 75C and in some cases even 90C insulation.....
I am sure that was also part of the argument.....it happens many times where someone asks how this or that happened....and the room goes silent.It makes no sense since there was no real world evidence of a problem despite millions of cables in service for decades.
interesting enough I can't seem to find the old study.....hmmmm...
but here is one I am sure you all have already.http://www.nfpa.org/~/media/files/n...oundation/damagedegradationnmcables.pdf?la=en
That's an interesting study. I still say there was no real world evidence of cable failures that merited a code change three or four cycles ago, and the most recent code change back to the way things used to be puts an exclamation mark on that.
Yup, hence why I ignored that rule completely. :thumbsup:
I ignored it as well, but mostly because I can't recall last time I ever touched "new" SE cable. Likely have touched existing cables a time or three in the past 6-10 years, but most of them were likely touched because they were being removed.It's posts like this that get you the hack title.
This was pushed by the wire and cable folks......Made sense since the conductors inside are more than likely 75C and in some cases even 90C insulation. The argument was that (and their still is not any known) type SE Cable was evaluated using the same specifications as Type NM-B and as such the 60C was to be used...due to their similarity. However, no one could produce anything for SE as tested like NM-B so that lack of information supported the face the inners are again rated for 75C or even 90C from some manufacturers.
The other argument was that normal Type NM-B also has conductors rated higher than 60C...but limited by 334.80 and based on tests that were done by NEMA and others. Not sure anyone will try to buck that pig next cycle..I sure am not.