Looking to hopefully clear this up. This seems pretty straightforward to me however I've been unable to find a black-and-white example either on forums, google, or by discussing with peers.
When sizing an instantaneous trip circuit breaker for motor branch circuit short-circuit and ground-fault protection, does 430.52(C)(1) Exception No. 1 apply that allows rounding up to the next standard size when the calculated size does not correspond to a standard size?
NEC 430.52(C)(3) states that instantaneous trip circuit breakers may be set to no more than the table 430.52 value:
However, 430.52(C)(1) Exception No. 1 allows rounding up to the next standard size when the applied table percentage does not correspond to a standard size:
For reference, this is based on the 2017 NEC, and assumes that the breaker size is adequate for starting (i.e., do not need to consider 430.52(C)(3) Exception No. 1).
Thanks for hopefully a fruitful discussion
.
When sizing an instantaneous trip circuit breaker for motor branch circuit short-circuit and ground-fault protection, does 430.52(C)(1) Exception No. 1 apply that allows rounding up to the next standard size when the calculated size does not correspond to a standard size?
NEC 430.52(C)(3) states that instantaneous trip circuit breakers may be set to no more than the table 430.52 value:
430.52(C)(3) Instantaneous Trip Circuit Breaker. An instantaneous trip circuit breaker shall be used only if adjustable and if part of a listed combination motor controller having coordinated motor overload and short-circuit and ground-fault protection in each conductor, and the setting is adjusted to no more than the value specified in Table 430.52.
However, 430.52(C)(1) Exception No. 1 allows rounding up to the next standard size when the applied table percentage does not correspond to a standard size:
430.52(C)(1) In Accordance with Table 430.52. Exception No. 1: Where the values for branch-circuit short-circuit and ground-fault protective devices determined by Table 430.52 do not correspond to the standard sizes or ratings of fuses, nonadjustable circuit breakers, thermal protective devices, or possible settings of adjustable circuit breakers, a higher size, rating, or possible setting that does not exceed the next higher standard ampere rating shall be permitted.
For reference, this is based on the 2017 NEC, and assumes that the breaker size is adequate for starting (i.e., do not need to consider 430.52(C)(3) Exception No. 1).
Thanks for hopefully a fruitful discussion