Hi everyone ,I have a question if someone would explain me , so I'm trying to understand the last part of Exception No 1 of 312.6(B) which says:
... provided the conductor enters or leaves the enclosure where the gutter joins an adjacent gutter that has a width that conform 312.6(b) for the conductors. From what i understand is that : the gutter from where the cables entry or leaves is adjacent with the gutter which should have a width conforms Table 312.6(B) for the conductors ...so that said is contrary to first part of this Exception No 1 of 312.6(B) which says to use Table 312.6(A) if the distance is in accordance with this table.
Thanks.
... provided the conductor enters or leaves the enclosure where the gutter joins an adjacent gutter that has a width that conform 312.6(b) for the conductors. From what i understand is that : the gutter from where the cables entry or leaves is adjacent with the gutter which should have a width conforms Table 312.6(B) for the conductors ...so that said is contrary to first part of this Exception No 1 of 312.6(B) which says to use Table 312.6(A) if the distance is in accordance with this table.
Thanks.