2017 nec residential AFCI locations

Status
Not open for further replies.

Todd0x1

Senior Member
Location
CA
I just want to make sure I have this correct. In a dwelling unit under 2017 nec, 15 and 20a 120v receptacles in: a walk in closet within an ensuite bathroom; a small sliding door closet in a bedroom; and in a dining room all need to be AFCI protected yes?
 

macmikeman

Senior Member
I just want to make sure I have this correct. In a dwelling unit under 2017 nec, 15 and 20a 120v receptacles in: a walk in closet within an ensuite bathroom; a small sliding door closet in a bedroom; and in a dining room all need to be AFCI protected yes?

I don't have a 17 handy but I don't think the bathroom circuit is required to be AFCI protected (in dwellings) for the 17 . The other locations you mentioned do.
 