2017 NEC vs 2020 NEC

Status
Not open for further replies.
Hello,

We have a project in North Texas. The City is in 2017 NEC and 2015 IRC.
We designed the system according to the 2017 NEC and 2015 IRC. Then the plan examiner passed the plan and permit.

The inspector failed us and asked us to follow the 2020 NEC and 2021 IRC, which will cost a lot of money.
Is this even legal? How do we approach this type of issue?
 
Last edited:

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
File an appeal, I have done it and prevailed ! ... Also, it caused them to change their enforcement policy
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
That's an easy one. Do a changer order and let GC and owner fix it.
As a rule if the permit was taken out prior to there change to 2020 than they usually honor it. If no change to 2020 don't understand how it can be enforceable.
I bet a phone call would fix the issue. If not a visit to there office might.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
The NEC has to legally adopted by your jurisdiction. There will be a process or document on how that is done
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If the permit was taken out and the 2017 code was implemented then they cannot enforce the 2020 Nec on your project
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Is this even legal?
Not here, or anywhere I know. The power that gives the AHJ the ability to enforce compliance with the code in effect at the time the permit was issued also denies him the ability to enforce anything else.

How do we approach this type of issue?
Climb the food chain. Ask him to get his supervisor involved. Be polite and civil, but also be firm.

An alternative would be to offer to do any changes he is willing to pay for.
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
This attachment is a detailed record of the NEC adoptions.
 

Attachments

  • NEC - Policy Institute Falling Behing Electrical SafetyReport #2.pdf
    763 KB · Views: 19
Status
Not open for further replies.
Top