Hello,
I have a question in regards to groupings of disconnects per 230.71(A) of the 2017 version. My current situation is this:
Existing building has 6 Service Disconnects "Grouped" that are tapped off of parallel sets of Underground service conductors in a junction box located below said grouped disconnects. I'm adding an additional PV System Disconnect as allowed in 230.40(Except. 5). The issue that I'm having is in regards to 230.71(A).
The verbiage states "There shall be not more than six SETS of disconnects per service grouped in any one location". It does not, however, say "There shall be not more than six disconnects per service grouped in any one location"
As far as I'm aware this PV System Disconnect would be part of its own SET of disconnects and therefore can be located near the original 6 grouped disconnects. Am I wrong? I'm having trouble finding an answer online as most responses don't deal with the additional number of SEC sets allowed. Also, most responses that I've found leave out the understanding that the verbiage of the NEC says SET of disconnects and not just disconnects. Additionally, SET is defined in the dictionary as "a number, group, or combination of things of similar nature, design, or function".
I have a question in regards to groupings of disconnects per 230.71(A) of the 2017 version. My current situation is this:
Existing building has 6 Service Disconnects "Grouped" that are tapped off of parallel sets of Underground service conductors in a junction box located below said grouped disconnects. I'm adding an additional PV System Disconnect as allowed in 230.40(Except. 5). The issue that I'm having is in regards to 230.71(A).
The verbiage states "There shall be not more than six SETS of disconnects per service grouped in any one location". It does not, however, say "There shall be not more than six disconnects per service grouped in any one location"
As far as I'm aware this PV System Disconnect would be part of its own SET of disconnects and therefore can be located near the original 6 grouped disconnects. Am I wrong? I'm having trouble finding an answer online as most responses don't deal with the additional number of SEC sets allowed. Also, most responses that I've found leave out the understanding that the verbiage of the NEC says SET of disconnects and not just disconnects. Additionally, SET is defined in the dictionary as "a number, group, or combination of things of similar nature, design, or function".