I'm working at an existing building where the service conductor feeders come into the building and terminate at the pull section of a switchboard. There are 6 existing service disconnects at the next section of the switchboard, thus the supply side connection.
There is room for one more set of feeders to lug on within this pull section which we plan on using as a connection point and then locate overcurrent protection within 16.5ft. of conductor length or 71ft if we used cable limiters per 705.11(C)
A lot of the language in 705.11talks about connections to the "service conductors", I'm assuming that the bus bar within the pull section is part of the service conductors. The bus is technically a bare conductor right?
If we couldn't connect at the bus we would have to somehow intercept the multiple sets of feeders with our single feeder set from our IEPPS which would require a piece of equipment before the switchboard which would pretty much kill this project from a financial standpoint. Maybe I'm just overthinking it.
There is room for one more set of feeders to lug on within this pull section which we plan on using as a connection point and then locate overcurrent protection within 16.5ft. of conductor length or 71ft if we used cable limiters per 705.11(C)
A lot of the language in 705.11talks about connections to the "service conductors", I'm assuming that the bus bar within the pull section is part of the service conductors. The bus is technically a bare conductor right?
If we couldn't connect at the bus we would have to somehow intercept the multiple sets of feeders with our single feeder set from our IEPPS which would require a piece of equipment before the switchboard which would pretty much kill this project from a financial standpoint. Maybe I'm just overthinking it.