2020 Exam Prep Calculation Question - Unit 10 Challenge Q's #27

Status
Not open for further replies.

paullmullen

Senior Member
Location
Wisconsin
Occupation
Electrical Engineer & Master Electrician
Here is Challenge Question 27 from Chapter 10 of the 2020 Exam Prep book.


1695608506087.png


My solution is 196A. Kinda close to (b) and kinda close to (a)

When I compare my solution to the one in the answer key, I get this:
My Solution
Answer Key
Match?
General Lighting Load
8040 VA​
8040 VA​
YES
Appliances
7380 VA​
7380 VA​
YES
Dryer
10,000 VA​
10,000 VA​
YES
Cooking Equipment
11,000 VA​
11,000 VA​
YES
AC vs Heat
10,710 VA​
10,000 VA​
NO


From that point on, the math is just broken because of the difference.

I think the problem is that the provided solution in the answer key ignores the fact that there are two air conditioners per unit. The only way I can get to the provided solution is to drop the number of air conditioners per unit to 1.



1695609778988.png



Here's my math:

1695609221215.png


What am I doing incorrectly?


Thanks,


Paul
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
Here is Challenge Question 27 from Chapter 10 of the 2020 Exam Prep book.


[...]


What am I doing incorrectly?
I dunno; assuming that whoever wrote the question and the answer knew what they were doing? :D
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
Would not omit the smaller of the two. The two ac units are 120 volt
Electrician heat is the larger of the two. Then the largest motor would be?
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
The question is not clear is 21A one airconditioner or both of them? If it is both, then the heat is the larger HVAC load. And in that case, what is the largest motor load to get hit with the extra 25% factor?
 

paullmullen

Senior Member
Location
Wisconsin
Occupation
Electrical Engineer & Master Electrician
Would not omit the smaller of the two. The two ac units are 120 volt
Electrician heat is the larger of the two. Then the largest motor would be?
Well, in fact the code does call for the smaller of the two (AC or Heat) to be omitted if they are not coincident: 220.60

1695669064076.png
 

paullmullen

Senior Member
Location
Wisconsin
Occupation
Electrical Engineer & Master Electrician
The question is not clear is 21A one airconditioner or both of them? If it is both, then the heat is the larger HVAC load. And in that case, what is the largest motor load to get hit with the extra 25% factor?
Well... the math in the solution seems to think that it is 21A for one unit, but you're right that the language of the question could be read two different ways. Hmmm...
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
Well, in fact the code does call for the smaller of the two (AC or Heat) to be omitted if they are not coincident: 220.60

View attachment 2567643
I did a typo and corrected later, sorry.
Man I missed a word above.
I would omit the smaller of the two.
Omit AC units. Use ele heat.
Ah... sure... omitting the smaller makes sense, but I think with 2 A/Cs per unit, the A/C load is the larger, right?
I would say no.
I read it as dwelling one ac load 21 amps@120v and heat @ 5kw
Total for both
Ac
21*1.25+21*120=5670
Heat
5000*2= 10,000
Omit the AC units.


What is key for me it does not say heat pumps. They may be window AC for all we know

What if each unit has 2500 kw of heat. I took it as totals.
Look at the key pic closely its doing total AC and heat load.
It's using 21*120 *1.25 then adding the 21.
It's lso using 5000*2
1695687535620.png
 

paullmullen

Senior Member
Location
Wisconsin
Occupation
Electrical Engineer & Master Electrician
I did a typo and corrected later, sorry.


I would say no.
I read it as dwelling one ac load 21 amps@120v and heat @ 5kw
Total for both
Ac
21*1.25+21*120=5670
Heat
5000*2= 10,000
Omit the AC units.


What is key for me it does not say heat pumps. They may be window AC for all we know

What if each unit has 2500 kw of heat. I took it as totals.
Look at the key pic closely its doing total AC and heat load.
It's using 21*120 *1.25 then adding the 21.
It's lso using 5000*2
View attachment 2567653
Sorry about the fake-out about "heat pumps". It's in my notes just in case, but it wasn't in the math here.

For sure, you've described the solution as done for the answer key, but when I read the question, it's not what I read.


Thanks for engaging.
 