Dsg319
Senior Member
- Location
- West Virginia
- Occupation
- Wv Master “lectrician”
Question is written, Where a 2 gang box contains two (2) single-pole switches, unless the box is equipped with permanently installed barriers, voltage between the adjacent switches shall not be in excess if________?
A. 120volts
B. 277volts
C. 480volts
D. 240volts
I was having problems locating the correct article to begin with (I know one should have thought to look under switches lol). BUT when I see the exam books answer they had chosen answer B. (277volts)
When I read the reference they used to get the answer, code language says.
404.8 (B)
A snap switch shall not be grouped or ganged in enclosures with other snap switched, receptacles, or similar devices. Unless they are arranged so that the voltage between adjacent devices does not exceed (300volts), or unless they are installed in enclosures equipped with identified, securely installed barriers between adjacent devices.
Shouldn’t 300volts have been the correct answer rather than 277volts?
A. 120volts
B. 277volts
C. 480volts
D. 240volts
I was having problems locating the correct article to begin with (I know one should have thought to look under switches lol). BUT when I see the exam books answer they had chosen answer B. (277volts)
When I read the reference they used to get the answer, code language says.
404.8 (B)
A snap switch shall not be grouped or ganged in enclosures with other snap switched, receptacles, or similar devices. Unless they are arranged so that the voltage between adjacent devices does not exceed (300volts), or unless they are installed in enclosures equipped with identified, securely installed barriers between adjacent devices.
Shouldn’t 300volts have been the correct answer rather than 277volts?