2020 master prep question

Status
Not open for further replies.

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
Question is asking for conductor ampacity for the following motor. My answer (could be wrong) does not come out to there’s. The way they done there’s is with the name plate current to find conductor ampacity.

I was always thought use nameplate current for OVERLOADS and FLC in the NEC for conductor ampacity.
 

Attachments

  • EB58E08C-2DB4-44AF-AD23-AC40B541777F.jpeg
    EB58E08C-2DB4-44AF-AD23-AC40B541777F.jpeg
    624.6 KB · Views: 40
  • 239CD6B9-5847-43C4-AA50-025980F8DE1C.jpeg
    239CD6B9-5847-43C4-AA50-025980F8DE1C.jpeg
    917.2 KB · Views: 36

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
Yes nameplate (hP) for overloads and FLC for conductor ampacity.
Yeah I’m guessing they either messed up on it, or I was missing something but not quite sure. Because to size shortcircuit/ground fault protection the nameplate (FLA) is pretty well irrelevant?
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
In this case you do use the nameplate. Look closely at 430.22(E) and the title of Table 430.22(E). Note that is says "nameplate".
 
Last edited by a moderator:

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
In this case you do use the nameplate. Look closely at 430.22(E) and the title of Table 432.22(E). Note that is says "nameplate".
Thank you! If it was a snake that one woulda bit me...
 

Attachments

  • ADC87D2A-363F-46CA-9A16-A57CE326B751.jpeg
    ADC87D2A-363F-46CA-9A16-A57CE326B751.jpeg
    483.3 KB · Views: 17

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
DAE3104E-BBA4-498F-ABF5-9D15302632B3.jpeg
When sizing a main breaker on feeder conductors supplying a panel full of motor loads, do I have it the correct understanding of sizing it by largest OCPD in the group plus the FLC of the rest of the motor circuits?

Not taking into consideration of not operating simultaneously....
 

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
Funny, I can no longer see your post relating to this.
Thanks. And the reason you can’t see the other post was it was I deleted it real quick because I shortly after asking found the answer.....was hoping no one noticed but guess I’m not that slick😛
 