Maybe some additional details regarding my design:
5 Story Building in Texas (municipality, multiuse building).
Service Transformer: 2000kVA 12.4k - 480/277V
At the building, I have a NEMA 3R service disconnect, with a built-in (factory installed) Type 1 SPD, which should satisfy 242.12(A) & (B).
Then my service enters the building and terminates at the Main Distribution Switchboard.
From there it goes to my 480V distribution panelboards (each floor).
Afterward, there are 480V - 208/120V utility transformer and 208/120V utility panelboards (each floor).
Per 242.14(C), it appears I need a Type 2 SPD within the 208/120V panelboards, correct?
Now that I re-read the entire 242 section, and Table 242.3, it does not appear I am required to have a SPD at the service entry. I would require one @ COPS, elevators/escalators, Fire Pump, IT equip, and modular data center (all of which are within the building). Maybe it is better to supply SPDs at the MDP & each utility panelboard rather than for each category listed (cover everything with SPD, so I don't have to worry about the individual needs)?
Thank you for your help with trying to interpret this new/rearranged NEC section.
Sincerely,
NSL