Would this apply to the requirements of 250.24(A)(1) having the GEC terminate at the grounded conductor bus ? If I’m not mistaken , unless you have a wire type or busbar connecting the grounded conductor buss and the EGC buss, the GEC must terminate at the grounded conductor buss? If a screw type main bonding jumper is installed , the GEC must terminate at the grounded conductor buss. Is the addition of 250.109 allowing the GEC to terminate on a lug attached to the case of the service disconnect enclosure if there is a screw type main bonding jumper installed? Thanks in advance.