250.25 Grounding Systems Permitted to Be Connected on the Supply Side of the Disconnect.
The grounding of systems connected on the supply side of the service disconnect, as permitted in
230.82, that are in enclosures separate from the service equipment enclosure shall comply with
250.25(A) or (B).
250.25(A) Grounded System.
If the utility supply system is grounded, the grounding of systems permitted to be connected on the supply side of the service disconnect and are installed in one or more separate enclosures from the service equipment enclosure shall comply with the requirements of
250.24(A) through (D).
250.25(B) Ungrounded Systems.
If the utility supply system is ungrounded, the grounding of systems permitted to be connected on the supply side of the service disconnect and are installed in one or more separate enclosures from the service equipment enclosure shall comply with the requirements of
250.24(E).