2020 NEC 250.50

redlinepilot15

New User
Location
Broward
Occupation
Inspector
Does a large steel reinforced Comercial AC equipment pad have to be bonded to the foundation steel / electrode grounding system? The pad is on the side of a new single story building.
 
IMO no. If it's likely to become energized then the EGC run to the equipment that may energize it would be sufficient to bond it.
 