2020 NEC 250.50

Merry Christmas

redlinepilot15

New User
Location
Broward
Occupation
Inspector
Does a large steel reinforced Comercial AC equipment pad have to be bonded to the foundation steel / electrode grounding system? The pad is on the side of a new single story building.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
IMO no. If it's likely to become energized then the EGC run to the equipment that may energize it would be sufficient to bond it.
 