R redlinepilot15 New User Location Broward Occupation Inspector Nov 19, 2024 #1 Does a large steel reinforced Comercial AC equipment pad have to be bonded to the foundation steel / electrode grounding system? The pad is on the side of a new single story building.
Does a large steel reinforced Comercial AC equipment pad have to be bonded to the foundation steel / electrode grounding system? The pad is on the side of a new single story building.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Nov 19, 2024 #2 IMO no. If it's likely to become energized then the EGC run to the equipment that may energize it would be sufficient to bond it.
IMO no. If it's likely to become energized then the EGC run to the equipment that may energize it would be sufficient to bond it.