NEC 625.41 requires AC OCPD to be sized to 125 percent of the maximum load of the EVSE equipment.
NEC 625.42 is related to DC conductor sizing downstream of AC OCPD. i.e. for example level 3 charging cabinet that feeds (2) separate downstream charging posts. The feeder between the cabinet and posts is DC.
Regarding 625.42, the article says "the power transfer equipment shall have sufficient rating to supply the load served. Electric vehicle charging loads shall be considered to be continuous loads for the purposes of this article. Service and feeder shall be sized in accordance with the product ratings. Where an automatic load management system is used, the maximum equipment load on a service and feeder shall be the maximum load permitted by the automatic load management system..."
Do you interpret this article to size DC conductors based on the maximum load listed on the datasheet (product rating) OR the maximum load listed on the datasheet x1.25? This is stemming from the statement in 625.42: "EV charging loads shall be considered to be continuous loads for the purposes of this article".
Thanks all
NEC 625.42 is related to DC conductor sizing downstream of AC OCPD. i.e. for example level 3 charging cabinet that feeds (2) separate downstream charging posts. The feeder between the cabinet and posts is DC.
Regarding 625.42, the article says "the power transfer equipment shall have sufficient rating to supply the load served. Electric vehicle charging loads shall be considered to be continuous loads for the purposes of this article. Service and feeder shall be sized in accordance with the product ratings. Where an automatic load management system is used, the maximum equipment load on a service and feeder shall be the maximum load permitted by the automatic load management system..."
Do you interpret this article to size DC conductors based on the maximum load listed on the datasheet (product rating) OR the maximum load listed on the datasheet x1.25? This is stemming from the statement in 625.42: "EV charging loads shall be considered to be continuous loads for the purposes of this article".
Thanks all