pvgreeze
Member
- Location
- Philadelphia
- Occupation
- Electrical Engineer
Don't these two sections completely contradict each other? Maybe I'm missing something extremely obvious here, but they're both one off sections that are pretty straight forward. Paraphrasing both, emphasizing points of confusion:
690.9(D): OCPD for a transformer with a source(s) on each side shall be provided per 450.3 considering first one side of the transformer then the other as the primary.
705.30(C): Transformer with sources on each side shall be provided OCPD per 450.3. The primary shall be the side connected to the largest source of fault current.
These seem to be saying the complete opposite of each other. Does 690 supersede 705 for PV specific installs given that 690 is exclusively for PV whereas 705 is general interconnected sources? What are your thoughts? For what its worth, I've always designed towards the interpretation of 705.30(C) - for PV, consider the utility side the primary, inverter side the secondary.
690.9(D): OCPD for a transformer with a source(s) on each side shall be provided per 450.3 considering first one side of the transformer then the other as the primary.
705.30(C): Transformer with sources on each side shall be provided OCPD per 450.3. The primary shall be the side connected to the largest source of fault current.
These seem to be saying the complete opposite of each other. Does 690 supersede 705 for PV specific installs given that 690 is exclusively for PV whereas 705 is general interconnected sources? What are your thoughts? For what its worth, I've always designed towards the interpretation of 705.30(C) - for PV, consider the utility side the primary, inverter side the secondary.