This section has been re-written a bit and the Table for SFD has been brought back and can be used if no adjustment factors are needed. Also the ampacity table number is back to T310.16 again.
310.12 Single-Phase Dwelling Services and Feeders.
For one-family dwellings and the individual dwelling units of two-family and multifamily dwellings, service and feeder conductors supplied by a single-phase, 120/240-volt system shall be permitted to be sized in accordance with 310.12(A) through (D).
For one-family dwellings and the individual dwelling units of two-family and multifamily dwellings, single-phase feeder conductors consisting of two ungrounded conductors and the neutral conductor from a 208Y/120 volt system shall be permitted to be sized in accordance with 310.12(A) through (C).
310.12(A) Services.
For a service rated 100 amperes through 400 amperes, the service conductors supplying the entire load associated with a one-family dwelling, or the service conductors supplying the entire load associated with an individual dwelling unit in a two-family or multifamily dwelling, shall be permitted to have an ampacity not less than 83 percent of the service rating. If no adjustment or correction factors are required, Table 310.12 shall be permitted to be applied.
310.12(B) Feeders.
For a feeder rated 100 amperes through 400 amperes, the feeder conductors supplying the entire load associated with a one-family dwelling, or the feeder conductors supplying the entire load associated with an individual dwelling unit in a two-family or multifamily dwelling, shall be permitted to have an ampacity not less than 83 percent of the feeder rating. If no adjustment or correction factors are required, Table 310.12 shall be permitted to be applied.
310.12(C) Feeder Ampacities.
In no case shall a feeder for an individual dwelling unit be required to have an ampacity greater than that specified in 310.12(A) or (B).
310.12(D) Grounded Conductors.
Grounded conductors shall be permitted to be sized smaller than the ungrounded conductors, if the requirements of 220.61 and 230.42 for service conductors or the requirements of 215.2 and 220.61 for feeder conductors are met.
Where correction or adjustment factors are required by 310.15(B) or (C), they shall be permitted to be applied to the ampacity associated with the temperature rating of the conductor.
Informational Note No. 1: The service or feeder ratings addressed by this section are based on the standard ampere ratings for fuses and inverse time circuit breakers from 240.6(A).
Informational Note No. 2: See Example D7 in Annex D.