2020 NEC - exhibit 250.12 for grounding
shespuzzling
new york
When I look at this exhibit, I see a return path for current back via the equipment ground path in a normal condition (marked up in red). Maybe my misunderstanding is that the connection I circled in blue isn’t necessarily a continuous path? Any help appreciated!
Thanks
Up to and including the main service disconnect enclosure, the neutral/grounded conductor and any metallic conduits, enclosures, troughs, other raceways, etc., are considered to be one and the same.
They, along with the grounding electrodes, establish, or re-establish the zero-volts reference point for the service and the premises equipment grounding system. That's "earth" for all intents and purposes.
Thank you, so it sounds like it’s true that current during a normal condition could return via the path I showed in red, but this is acceptable by code for this specific situation since we are service equipment?
If that’s true, could that lead to shock potential if a person touched the service trough (for example) and there was current flowing through it?
Yes it's acceptable and required to connect all of the metal parts upstream of the service disconnect to the neutral.
Under normal conditions there should be no shock potential.
The only voltage to provide a shock hazard would be the voltage drop as a result of the current flow on that path. Very unlikely that there will be enough voltage drop to result in a shock hazard.
Absolutely.
Read my second paragraph again.