2022: Any 400A bus, Solar Ready or not, load centers without meter available?

Status
Not open for further replies.

nobodytoo

Member
Location
LAX
Occupation
scientist/engineer
We are in 2022,we have solar, we have EV, PV, PW and more, etc. - even the 200A service from electric company needs a bus that can carry the current from PV, battery or generator, in all directions.
SO as the min I was asked fora 400A bus, 200 disconnect breaker for near term PV solar addition and battery - all back feeding to the grid.
What load center to install today in order to avoid another replacement in 2 to 3 years.
 
You can order a panelboard with whatever you want. For example I use Siemens panelboards and you can get a P1 with a 200A breaker and either a 250 or 400A bus, and they are so much nicer than a load center. Load center type panel boards over 225A are not that common.
 