I am a new EIT(1yr)(Just passed my PE today) in consulting and am trying to understand 250.122(B). I made a calculator in Excel to help with this, and in applying it to a recent project I encountered a scenario that I am not 100% sure how to handle. I have a workaround that I believe addresses this and want to pick brains to see if I'm on the right track.
Scenario: I have a 400A breaker feeding a 208 3phase load at 220ft away. Without regarding voltage drop, the minimum conductor size is 600kcmil per 310.16
Now, upsizing for voltage drop we must increase the size to 750kcmil. This represents a 25% increase in wire size and thus would proportionally increase EGC from #3 to #2.
So far so good.
However, we want to avoid using cables larger than 600kcmil (Something about the difficulty of installation I am told) and thus we are going to run parallel conduits.
With (2) runs of cable, I can size for voltage drop sufficiently with #4/0 wire. The tricky part comes when you try to determine what the EGC should be. Looking at kcmil, we went from 600kcmil to 423kcmil, for a decrease in wire area. NEC 250.122(F)(2)(a) "...The Equipment grounding conductor in each multiconductor cable shall be sized in accordance with 250.122...", so we know it cannot be smaller than #3. However, since our kcmil decreased it is not immediately clear how to proceed.
My workaround goes as follows:
Since we are going from a single cable run to a dual cable run, our baseline should be based upon a dual cable run, pre-voltage drop.
(2) runs of #3/0 are sufficient for a 400A load per 310.16. So our base is (2) sets of #3/0 with #3 EGC.
Upsizing for voltage drop to (2) runs of #4/0 gives us an increase of 26%, dictating the need to upsize our EGC to #2.
This seems to fit the spirit of the rule and provides similar results to the original scenario.
Am I on the right track, or is there something I am missing?
Scenario: I have a 400A breaker feeding a 208 3phase load at 220ft away. Without regarding voltage drop, the minimum conductor size is 600kcmil per 310.16
Now, upsizing for voltage drop we must increase the size to 750kcmil. This represents a 25% increase in wire size and thus would proportionally increase EGC from #3 to #2.
So far so good.
However, we want to avoid using cables larger than 600kcmil (Something about the difficulty of installation I am told) and thus we are going to run parallel conduits.
With (2) runs of cable, I can size for voltage drop sufficiently with #4/0 wire. The tricky part comes when you try to determine what the EGC should be. Looking at kcmil, we went from 600kcmil to 423kcmil, for a decrease in wire area. NEC 250.122(F)(2)(a) "...The Equipment grounding conductor in each multiconductor cable shall be sized in accordance with 250.122...", so we know it cannot be smaller than #3. However, since our kcmil decreased it is not immediately clear how to proceed.
My workaround goes as follows:
Since we are going from a single cable run to a dual cable run, our baseline should be based upon a dual cable run, pre-voltage drop.
(2) runs of #3/0 are sufficient for a 400A load per 310.16. So our base is (2) sets of #3/0 with #3 EGC.
Upsizing for voltage drop to (2) runs of #4/0 gives us an increase of 26%, dictating the need to upsize our EGC to #2.
This seems to fit the spirit of the rule and provides similar results to the original scenario.
Am I on the right track, or is there something I am missing?