steve952
Member
- Location
- Southern California
- Occupation
- Electrician
New section 250.645(G) in the 2023 NEC States: "Grounding Electrode Conductors shall not be installed thru a ventilation opening of an enclosure." I understand the provision to prevent simply running a bare or insulated conductor thru the opening, but what about cutting a 7/8" hole and installing a fitting for an armored cable, would that be permissible?
On many projects we typically install a section of rebar (UFER) or a ground rod underneath the transformer and that UFER or Rod extends thru the bottom panel of the transformer and into the transformer enclosure. Would this be permitted?
The section doesn't say anything about ungrounded conductors, or equipment bonding conductors, or even grounded conductors passing thru the ventilation openings and I can't find another section in the NEC restricting those conductors from being installed thru the openings.
I assume this was to prevent the installation of bare or insulated conductors only and not to prohibit other raceways from entering the bottom of transformer enclosures. Keep in mind most floor mounted transformers don't have much room on the bottom that isn't ventilated, so this may complicate some installations.
On many projects we typically install a section of rebar (UFER) or a ground rod underneath the transformer and that UFER or Rod extends thru the bottom panel of the transformer and into the transformer enclosure. Would this be permitted?
The section doesn't say anything about ungrounded conductors, or equipment bonding conductors, or even grounded conductors passing thru the ventilation openings and I can't find another section in the NEC restricting those conductors from being installed thru the openings.
I assume this was to prevent the installation of bare or insulated conductors only and not to prohibit other raceways from entering the bottom of transformer enclosures. Keep in mind most floor mounted transformers don't have much room on the bottom that isn't ventilated, so this may complicate some installations.