wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
Seems to me that subsections (3) and (4) don't match the commonly understood intentions, and would be better worded as:
(3) For wiring in wet, dampdry, or corrosive locations.
(4) In dry locations, where installedInstalled as nonmetallic-sheathed cable. Where so installed, the The installation and conductor requirements shall comply with Parts II and III of Article 334 and shall be of the multiconductor type.
As currently worded, subsection (4) is meaningless, as subsection (3) provides a blanket allowance for dry locations. And the allowance for damp locations seems to be missing.
Cheers, Wayne
(3) For wiring in wet, damp
(4) In dry locations, where installed
As currently worded, subsection (4) is meaningless, as subsection (3) provides a blanket allowance for dry locations. And the allowance for damp locations seems to be missing.
Cheers, Wayne