Currently NEC language requires both countertop receptacles and wall space receptacles along kitchen walls with base cabinets and countertops, yet surely this is not the intent, nor is anyone doing this, to my knowledge. This PI fixes this.
Cheers, Wayne
210.52(C) Countertops and Work Surfaces.
In kitchens, pantries, breakfast rooms, dining rooms, and similar areas of dwelling units, receptacle outlets for countertop and work surfaces that are 300 mm (12 in.) or wider shall be installed in accordance with 210.52(C)(1) through (C)(3) and shall not be considered as the receptacle outlets required by 210.52(A) for wall spaces without countertops or work surfaces.
For the purposes of this section, where using multioutlet assemblies, each 300 mm (12 in.) of multioutlet assembly containing two or more receptacles installed in individual or continuous lengths shall be considered to be one receptacle outlet.
Statement
In the 2014 NEC, 210.52(A)(2)(1) defined the wall spaces that require 210.52(A) receptacles as "Any space 600 mm (2 ft) or more in width (including space measured around corners) and unbroken along the floor line by doorways and similar openings, fireplaces, and fixed cabinets." In kitchens, this had the effect of excluding any portion of a wall with base cabinets, so no wall space receptacles were required there. We can say that the 210.52(A) wall zone and the 210.52(C) wall zone did not overlap.
In the 2017 NEC, 210.52(A)(2)(1) was amended so that it now ends ". . . and fixed cabinets that do not have countertops or similar work surfaces." This change means that for a kitchen wall space with fixed cabinets with a countertop, that wall space now does requires 210.52(A) receptacles. The 210.52(A) wall zone and the 210.52(C) wall zone now do overlap.
Moreover, the language in 210.52(C) requires that a receptacle installed to satisfy 210.52(C) may not be used to satisfy 210.52(A). The result is that a 6' length of wall countertop in a kitchen, located between fixed cabinets that extend to the ceiling without countertops, actually requires at least three receptacles to satisfy 210.52--two receptacles at appropriate locations to satisfy 210.52(C), and one additional receptacle to satisfy 210.52(A).
I doubt that this is in the intention. Therefore the proposed language change to 210.52(C) clarifies that the 210.52(C) receptacles may count as the 210.52(A) receptacles within the 210.52(C) wall zone.
Cheers, Wayne
210.52(C) Countertops and Work Surfaces.
In kitchens, pantries, breakfast rooms, dining rooms, and similar areas of dwelling units, receptacle outlets for countertop and work surfaces that are 300 mm (12 in.) or wider shall be installed in accordance with 210.52(C)(1) through (C)(3) and shall not be considered as the receptacle outlets required by 210.52(A) for wall spaces without countertops or work surfaces.
For the purposes of this section, where using multioutlet assemblies, each 300 mm (12 in.) of multioutlet assembly containing two or more receptacles installed in individual or continuous lengths shall be considered to be one receptacle outlet.
Statement
In the 2014 NEC, 210.52(A)(2)(1) defined the wall spaces that require 210.52(A) receptacles as "Any space 600 mm (2 ft) or more in width (including space measured around corners) and unbroken along the floor line by doorways and similar openings, fireplaces, and fixed cabinets." In kitchens, this had the effect of excluding any portion of a wall with base cabinets, so no wall space receptacles were required there. We can say that the 210.52(A) wall zone and the 210.52(C) wall zone did not overlap.
In the 2017 NEC, 210.52(A)(2)(1) was amended so that it now ends ". . . and fixed cabinets that do not have countertops or similar work surfaces." This change means that for a kitchen wall space with fixed cabinets with a countertop, that wall space now does requires 210.52(A) receptacles. The 210.52(A) wall zone and the 210.52(C) wall zone now do overlap.
Moreover, the language in 210.52(C) requires that a receptacle installed to satisfy 210.52(C) may not be used to satisfy 210.52(A). The result is that a 6' length of wall countertop in a kitchen, located between fixed cabinets that extend to the ceiling without countertops, actually requires at least three receptacles to satisfy 210.52--two receptacles at appropriate locations to satisfy 210.52(C), and one additional receptacle to satisfy 210.52(A).
I doubt that this is in the intention. Therefore the proposed language change to 210.52(C) clarifies that the 210.52(C) receptacles may count as the 210.52(A) receptacles within the 210.52(C) wall zone.