208Δ to 277/480Y Transformer installation issues

Status
Not open for further replies.

ThaddeusW

Member
Location
New York, NY
We are installing a new 480V machine in our facility with 120/208Y service. Our electrician installed a 75KVA 208Δ to 277/480Y transformer to power the machine. Machine has a 90A disconnect and no 277V line to neutral loads, it's all line-line. The transformer is fed by a 200A breaker from a sub panel which is next to and fed from the main switchboard by a 250A breaker. In my past life I was an electrician (I do industrial automation now) and I took a look at his initial wiring which was incorrect. Originally he had the transformer feeder EGC hooked to the secondary neutral bar, no secondary neutral bond to the transformer case, and no neutral connection to the building ground (GEC). I told him to move the feeder EGC to the case ground lug, hook a bonding jumper from another case lug to the secondary's neutral bar, and a GEC connection which he made to the main ground rod which happens to be the main ground rod for the switch board.

He was hesitant to bond the neutral to the case and GEC as he claimed the transformer creates it own ground, which is false if no bonding is in place as its a SDS. He also ignored my request for the bonding jumper and the GEC conductor to be separately connected to the neutral bar and instead hooked the GEC to an external ground lug supplied by the transformer manufacturer making the GEC connection share the neutral to case bonding jumper. After everything was in place, he flipped the feeder breaker and pop, it immediatly tripped. He again tried flipping it on and again it popped. In a huff he said "It's that stupid wire from the neutral to the case, there are too many grounds!" He removes the neutral bond jumper goes back and successfully flips the transformer feeder on. "See I told you that wire was no good! I've been doing this for 40 years." He measures the line-line and line-neutral voltages and everything checks out.

I couldnt' let that go and decided to look over everything again. With the feeder breaker off I lifted the single secondary neutral connection he made and megged the transformer to ground which was infinite indicating no line faults. I double checked everything and see no reason for the feeder breaker to trip with that neutral bonding jumper in place. Since the 480V machine is located 60 feet from the transformer, I had him install a 480V fused disconnect next to the transformer. That disconnect was in the off position and had the fuses removed at the time he tried energizing the transformer. Since there is no need for a neutral, he ran a #6 EGC from the transformer secondary neutral to the fused disconnect and off again to the machine. In the disconnect, he bonded the EGC to the case which will cause a parallel path to the transformer if the neutral jumper was in place. My thought it he could bring the GEC to the disconnect and bond everything in there.

My only conclusion for the tripping is the breaker he sized is too small for the transformer inrush current and somehow on his third and final try, got lucky. The removal of the neutral jumper was just coincidence. The 200A feeder is too small and should be sized for 125% which would be ~260A which would be up-sized to the next breaker size of 300A. Problem is, the panel box won't take a breaker bigger than 225A (GE style Q line) and the Siemens 1200A switch board has a maximum branch breaker rating of 250A. The sub panel is already occupied by an 80 and 60 amp three phase breaker and overloaded. He did agree that he should move the transformer feed from the sub panel to the switch board where there is one remaining space for a branch breaker. That might solve our problem but we are still under the 260A 125% rule though not by much.

Any thoughts? I think he got lucky and the bonding jumper had nothing to do with it and it was all related to the undersized feeder breaker.

Basic diagram of our setup for reference:
646transformer.jpg
 
Since there is no need for a neutral, he ran a #6 EGC from the transformer secondary neutral to the fused disconnect and off again to the machine. In the disconnect, he bonded the EGC to the case which will cause a parallel path to the transformer if the neutral jumper was in place.
View attachment 15903

The equipment grounding conductor should be tied to the disconnect.

7-18-13CodeQ%26Aweb2.jpg


By neutral jumper do you mean system bonding jumper?

Most of your questions can be answered here:

http://ecmweb.com/code-basics/grounding-and-bonding-separately-derived-systems

It sounds like inrush tripping to me.

Welcome to the forum!!
 
How does that graphic apply, when you have conductors spliced inside a conduit body?

I dont believe it does:


250.148 Continuity and Attachment of Equipment
Grounding Conductors to Boxes. Where circuit conductors
are spliced within a box, or terminated on equipment
within or supported by a box, any equipment grounding
conductor(s) associated with those circuit conductors shall
be connected within the box or to the box with devices
suitable for the use in accordance with 250.148(A) through
(E).
Exception: The equipment grounding conductor permitted
in 250.146(D) shall not be required to be connected to the
other equipment grounding conductors or to the box.
 
We are installing a new 480V machine in our facility with 120/208Y service. Our electrician installed a 75KVA 208Δ to 277/480Y transformer to power the machine. Machine has a 90A disconnect and no 277V line to neutral loads, it's all line-line. The transformer is fed by a 200A breaker from a sub panel which is next to and fed from the main switchboard by a 250A breaker. In my past life I was an electrician (I do industrial automation now) and I took a look at his initial wiring which was incorrect. Originally he had the transformer feeder EGC hooked to the secondary neutral bar, no secondary neutral bond to the transformer case, and no neutral connection to the building ground (GEC). I told him to move the feeder EGC to the case ground lug, hook a bonding jumper from another case lug to the secondary's neutral bar, and a GEC connection which he made to the main ground rod which happens to be the main ground rod for the switch board.

He was hesitant to bond the neutral to the case and GEC as he claimed the transformer creates it own ground, which is false if no bonding is in place as its a SDS. He also ignored my request for the bonding jumper and the GEC conductor to be separately connected to the neutral bar and instead hooked the GEC to an external ground lug supplied by the transformer manufacturer making the GEC connection share the neutral to case bonding jumper. After everything was in place, he flipped the feeder breaker and pop, it immediatly tripped. He again tried flipping it on and again it popped. In a huff he said "It's that stupid wire from the neutral to the case, there are too many grounds!" He removes the neutral bond jumper goes back and successfully flips the transformer feeder on. "See I told you that wire was no good! I've been doing this for 40 years." He measures the line-line and line-neutral voltages and everything checks out.

I couldnt' let that go and decided to look over everything again. With the feeder breaker off I lifted the single secondary neutral connection he made and megged the transformer to ground which was infinite indicating no line faults. I double checked everything and see no reason for the feeder breaker to trip with that neutral bonding jumper in place. Since the 480V machine is located 60 feet from the transformer, I had him install a 480V fused disconnect next to the transformer. That disconnect was in the off position and had the fuses removed at the time he tried energizing the transformer. Since there is no need for a neutral, he ran a #6 EGC from the transformer secondary neutral to the fused disconnect and off again to the machine. In the disconnect, he bonded the EGC to the case which will cause a parallel path to the transformer if the neutral jumper was in place. My thought it he could bring the GEC to the disconnect and bond everything in there.

My only conclusion for the tripping is the breaker he sized is too small for the transformer inrush current and somehow on his third and final try, got lucky. The removal of the neutral jumper was just coincidence. The 200A feeder is too small and should be sized for 125% which would be ~260A which would be up-sized to the next breaker size of 300A. Problem is, the panel box won't take a breaker bigger than 225A (GE style Q line) and the Siemens 1200A switch board has a maximum branch breaker rating of 250A. The sub panel is already occupied by an 80 and 60 amp three phase breaker and overloaded. He did agree that he should move the transformer feed from the sub panel to the switch board where there is one remaining space for a branch breaker. That might solve our problem but we are still under the 260A 125% rule though not by much.

Any thoughts? I think he got lucky and the bonding jumper had nothing to do with it and it was all related to the undersized feeder breaker.

Basic diagram of our setup for reference:
View attachment 15903

My thoughts are that you have an electrician that does not grasp the basic concepts of the NEC or electrical theory let alone the fine points of a compliant install.
You could very well be correct as to the cause of the primary breaker tripping especially if this xformer is a new one built to the latest energy standards. If you are on the edge this can be hit or miss. This is a growing industry problem due to these new xformer designs. I would agree that a 300 amp breaker would have been more appropriate. Unfortunately this puts you in a larger frame size. I think I would be inclined to try a 225 and hope for the best.
 
Thanks for the welcome! And I appreciate the help.

My thoughts are that you have an electrician that does not grasp the basic concepts of the NEC or electrical theory let alone the fine points of a compliant install.
You could very well be correct as to the cause of the primary breaker tripping especially if this xformer is a new one built to the latest energy standards. If you are on the edge this can be hit or miss. This is a growing industry problem due to these new xformer designs. I would agree that a 300 amp breaker would have been more appropriate. Unfortunately this puts you in a larger frame size. I think I would be inclined to try a 225 and hope for the best.

I think you pointed me in the right direction. It's a new Hammond DoE certified transformer. I assume the DoE efficiency requirements force the transformer manufacturer to lower the primary impedance to lower primary core losses with the side effect of larger inrush currents. We installed two other 208->480 xformers about 5 years ago without issue so I assume this must be the case.

We can run the transformer directly to the switchboard as it has a free space for an MCB but the frame size limits us to 250A. So we ordered a 250A MCB for the switchboard and it appears to have a trip delay adjust. Thankfully the sub panel is only a few feet from switch board so we don't have to change conductor size.

I'll update my post once we get the MCB in and wire the xformer to it.

As for our "electrician", lets just use the words retired and nepotism to describe him. Nice guy though...
 
As mentioned it is probably inrush that trips the 200A breaker.

75kVA @ 208V 3 phase is 208A. Due to Inrush, we often size the primary breaker at 125% FLA minimum but often 150%.
 
As mentioned it is probably inrush that trips the 200A breaker.

75kVA @ 208V 3 phase is 208A. Due to Inrush, we often size the primary breaker at 125% FLA minimum but often 150%.
With the secondary fused at 90A (which is the rated transformer secondary current), and assuming the other secondary conductor requirements of 240.21(C) are in compliance, the primary could be protected at up to 250% (520A, 600A upsized to next standard rating).

Seems a bit odd to me that the 1200A switchgear has a 250A branch breaker limit.
 
Seems a bit odd to me that the 1200A switchgear has a 250A branch breaker limit.

Sometimes it is just the way the spaces available are lined up. For example on I-Line panelboards or SWBDs, sometimes the left side is limited to a certain maximum frame size and the right side can handle bigger (if not already fully occupied)
 
Thanks for the welcome! And I appreciate the help.



I think you pointed me in the right direction. It's a new Hammond DoE certified transformer. I assume the DoE efficiency requirements force the transformer manufacturer to lower the primary impedance to lower primary core losses with the side effect of larger inrush currents. We installed two other 208->480 xformers about 5 years ago without issue so I assume this must be the case.

We can run the transformer directly to the switchboard as it has a free space for an MCB but the frame size limits us to 250A. So we ordered a 250A MCB for the switchboard and it appears to have a trip delay adjust. Thankfully the sub panel is only a few feet from switch board so we don't have to change conductor size.

I'll update my post once we get the MCB in and wire the xformer to it.

As for our "electrician", lets just use the words retired and nepotism to describe him. Nice guy though...
That is probably a magnetic trip adjustment and not so much a time delay mechanism.
 
With the secondary fused at 90A (which is the rated transformer secondary current), and assuming the other secondary conductor requirements of 240.21(C) are in compliance, the primary could be protected at up to 250% (520A, 600A upsized to next standard rating).

Seems a bit odd to me that the 1200A switchgear has a 250A branch breaker limit.

Cow called it. It's Siemens Switchboard. It is strange but when the system was installed, all the machinery was 208V and loads were few making 250A more than adequate. Now we are expanding and the machinery is all coming 480V standard making this transformer thing a headache. Hopefully, next year we are going to do a major service upgrade including a 480V service.

I see the 250A limit a lot in the Siemens gear we buy.
Correct! It is a Siemens switchboard.
 