What is the advantage, (if any) of only using single phase 208 vs 3 phase? I have 20 years of HVAC experience, but I am dumb as a carrot when it comes to the finer points like this.
What is the advantage, (if any) of only using single phase 208 vs 3 phase? I have 20 years of HVAC experience, but I am dumb as a carrot when it comes to the finer points like this.
Initial equipment investment is what can be different. Efficiency is a different ballgame.If you have motors that are going to run continuously (like say a day camp facility that has several swimming pools utilizing about 12 pool pump motors total) those motors will run more efficiently than if they were running on 120V or 208V, 1 phase. If you look at the nameplate ratings on a pool motor as an example (even for a residence), it will show the difference between running it at 120V and 230V. So, let's say that a simple residential pool motor if wired for on 120V will operate at 10 A, if you wired it and used 240V it will operate at 5A. When you have a commercial application and if you used a similar style and rated motor (only a 3-phase type) it will run at something less than 5A (probably 3.3A or something close).
Capacitors, start switches, potential relays - are a big maintenance issue at times. If you have limited load, seasonal load, etc. may still not be worth paying POCO extra every month or the initial investment for a three phase supply.anecdotal, I realize. For some time I worked for a large industrial complex with hundreds of motors. The single phase ones failed 5 to 1 over the 3 phase, usually capacitors or start switches.