Of course; poorly worded.adrian33773 said:Actually the maximum ocp device (breaker or fuse) protecting that panel can not exceed 225 amps for that 225 amp rated panel. You can make the feeders as large as you want.
adrian33773 said:I would say if the panel is rated for 225 amps, that would be the maximum main disconnect ocp allowed in that panel. That would be a 225 amp 3-pole breaker. Correct me if I'm wrong. The feeders would have to be sized according to the size of the main disconnect breaker. So if you only need a 150 amp service then you would put in a 150 amp main 3-pole breaker and size the feeders to 150 amps. You don't have to use the full capacity of the panel.
?Over Current Protection.? Sometimes a "D" for "Device" appears as well (i.e., OCPD). It might mean the main breaker on the panel or the breaker supplying the feeder. It depends on the context of the sentence.mmcampbe said:What does OCP stand for? I'm assuming it is the main breaker on the panel.
It does not make physical sense to speak of ?current between phases.? Current flows out of a panel on one phase conductor, and after having passed through the load it flows back into the panel on another phase conductor. But current is measured as it passes through any single conductor, not from one conductor to another.mmcampbe said:Is this the max current on the feeding cables or between the phases?
. . . or even two or all three simultaneously.charlie b said:The 225 amp rating is the maximum amount of current that can be allowed to flow on any of the three phase conductors.
charlie b said:The 225 amp rating is the maximum amount of current that can be allowed to flow on any of the three phase conductors.
The 225 amp rating is the maximum continuous current allowed per pole. Current exceeding the rating is permitted for short durations, such as motor starting or transformer in-rush.LarryFine said:. . . or even two or all three simultaneously.
oscarmal said:Actually check the switch gear to find out what is feeding your panel --fuse protection. If 225 amp fuses are are being used than you are covered at 225 less 80% between phases so (225amps * 80% = 180amps)